I assume you mean current and kWh?I was going to use the Poco bills for the last year to show loads on an existing building that is having an addition put on, my question is with the kw for the month do you divide by voltage alone or x 1.73. This is 3 phase
You can't determine current from kWh alone.
Do all three phases take equal currents?
Do they all have the same power factor?
If the answer to either is no, you can't calculate the currents.
jraef: If you have 1,000,000W for 1 hour, that's 1 MWh, right?
Noob123 (name changed to protect the innocent): Right.
jraef: But if you have 1W for 1,000,000 hours, that's still 1 MWh right?
Noob123: Right
jraef: So how can you determine the demand from a reading on the bill that just says 1MWh?
Noob123: You are reading too much into it. The peak demand in that situation is 1MW, so if the voltage was 480V 3 phase and .8pf, the peak current would be 1500A.
Yes, The demand is listed. I just wasn't sure on changing that number over to amps. I know the method for a service calc. but wasn't sure on a meter reading, what had me asking was their peak demand was around 450amps and the building has a 1600amp service.
Thanks
Sorry, The highest demand was 143.5 kw
Demand charges are almost always based on the average for a 15 minute period.
True, but that meets the requirements of 220.87 (2011)