ERIC LEDBETTER
We need to pull feeders to a 100 amp panel the run is 320 feet long 208 volt what do you think 4 #1 with a #3 ground :dunce:
How can you say that if you don't know what the load is?straight 208 3 phase?
Your selection will give you over 4% voltage drop
Ray C. Mullin had a slightly different equation using CMs and gave different answers, than, for example, by assuming #10 has 1 ohm/1000' (and #20 having 10 ohms/1000', and so on, up).Maybe you should calculate it yourself.
How to calculate voltage dropIn situations where the circuit conductors span large distances, the voltage drop is calculated. If the voltage drop is too great, the circuit conductor must be increased to maintain the current between the points. The calculations for a single-phase circuit and a three-phase circuit differ slightly. Single-phase voltage drop calculation:
Three-phase voltage drop calculation:
VD = Voltage drop (conductor temp of 75?C) in volts
VD% = Percentage of voltage drop (VD ? source voltage x 100). It is this value that is commonly called "voltage drop" and is cited in the NEC 215.2(A)(4) and throughout the NEC.
L = One-way length of the circuit's feeder (in feet)
R = Resistance factor per NEC Chapter 9, Table 8, in ohm/kft
I = Load current (in amperes)
Source voltage = The voltage of the branch circuit at the source of power. Typically the source voltage is either 120, 208, 240, 277, or 480 V.
Important Note: According to NEC 215.2(A)(4) informational note No. 2, the voltage drop for feeders should not exceed 3% and the voltage drop for branch circuits should not exceed 5%, for efficient operation.[4]
I don't know, the derivation wasn't shown.My program gave the following L to N
4.81 V @ 1.0 PF
4.96 V @ 0.9 pf
4.74 v @ 0.8 pf
Is Rays equation R cos A + X sin A where A is the
PF angle?
0.09827 |
That's just it isn't it. 100 amps, eighty amps, twenty? Who knows!!??I'm guessing that he used 100 amps but Eric mentioned 80% so maybe the load is 80 amps.
One thing is for sure, a hundred amp panel does not equal a hundred amps of load. And until you know what the load is what good is a voltage drop calculation?