The VFD controls a 300HP motor, 480V, 3 phase.  The VFD draws 385Amps.  The motor FLA is 357 Amps  The designer wishes to protect the VFD with a 400A 100 percent breaker, but he says that the feed from the vfd to the motor has to be 125% of the draw which will get it to 481 Amps and he would need at least 2 sets of 4/0 (and not with one set of 600KCM)
Would appreciate your comments regarding the breaker and cable sizes
	
		
			
		
		
	
				