DSeitz56
New member
- Bentonville, AR USA
Does the NEC allow for diversity for Instantaneous Electric Water Heaters when calculating load?
220.53 Appliance Load ? Dwelling Unit(s).
It shall be permissible to apply a demand factor of 75 percent to the nameplate rating load of four or more appliances fastened in place, other than electric ranges, clothes dryers, space-heating equipment, or air-conditioning equipment, that are served by the same feeder or service in a one-family, two-family, or multifamily dwelling.
The ironic thing about instantaneous water heaters is that, even though they draw about 1.21 Giga-Watts, you can save energy because they have no losses from maintaining a 30-50 gallon tank at 120 degrees.
Which I have measured at about 50w. This would cost me $66/yr.you can save energy because they have no losses from maintaining a 30-50 gallon tank at 120 degrees.
I put an hour meter on my 50 gallon 4500 watt electric water heater and found that it runs about 3.61 hours a day on average for a 60 day period starting from october to now. Looking at different size units for individual rooms and whole house units, i couldn't beat the 50 gallon unit with my 5 member family.
I put an analog clock between the neutral and a hot lead, set to midnight when everyone went to bed, and the next morning it advanced 5 minutes in 5 hours (B4 I added insulation) and 5 minutes in 7 hours, after.
5 min/5 hours x 4500w = 75w.
Any thoughts to Demand Charges that are coming with these new smart meters?
@KBSparky - the clock between neutral/ground and a hot lead is how I currently believe I should have done it way back when, but from what you say this won't work.
I can't recall whether I used the dropping resistors because I took the element backfeed into account, way back when.Only way it works is to use relay, or some other control method, or a 240 volt connected clock - which sounds like you attempted by putting resistors in series with a 120 volt clock. Two identical 120 volt clocks in series should work also. Just connecting to one element lead and a grounded conductor and leaving everything else as is will result in clock running continuously because the normal control only opens one lead of the 240 volts. you will always have back feed from the other side of the 240 volts through the element. Element resistance is low enough it may have little effect on accurate operation of the clock.
Close.they draw about 1.21 Giga-Watts,
It will eventually lead to higher rates for those with the higher demands, as it should. A reduced utilization factor means less efficient use of facilities.Any thoughts to Demand Charges that are coming with these new smart meters?