mstrlucky74
Senior Member
- Location
- NJ
Even with barriers can you have 24v wiring and 120v wiring in the same pull box per NEC? You would in a floor box with teledatsa outlet and recpt so I don't see why not. Thanks.
314.28(D) Permanent Barriers. Where permanent barriers are
installed in a box, each section shall be considered as a
separate box.
Even with barriers can you have 24v wiring and 120v wiring in the same pull box per NEC? You would in a floor box with teledatsa outlet and recpt so I don't see why not. Thanks.
you can have any voltages in a box, or conduit you wish,
as long as ALL insulation is rated for the highest voltage present.
That would not be true if the 24volt circuits were from a class 2 or class 3 system. Regardless of their insulation value they cannot occupy the same raceway or box as power conductors.
Even with barriers?
Even with barriers?
Let me throw a wrench in the gears.
How is is possible to supply a 24 volt contactor coil from a class 2 circuit and also connect to the power terminals of same contactor if they are to be in separate enclosures?
You do so in accordance with 725.136(D).
Chris
You do so in accordance with 725.136(D).
Chris