Even with barriers can you have 24v wiring and 120v wiring in the same pull box per NEC? You would in a floor box with teledatsa outlet and recpt so I don't see why not. Thanks.
314.28(D) Permanent Barriers. Where permanent barriers are
installed in a box, each section shall be considered as a
separate box.
Even with barriers can you have 24v wiring and 120v wiring in the same pull box per NEC? You would in a floor box with teledatsa outlet and recpt so I don't see why not. Thanks.
you can have any voltages in a box, or conduit you wish,
as long as ALL insulation is rated for the highest voltage present.
That would not be true if the 24volt circuits were from a class 2 or class 3 system. Regardless of their insulation value they cannot occupy the same raceway or box as power conductors.
Even with barriers?
Let me throw a wrench in the gears.
How is is possible to supply a 24 volt contactor coil from a class 2 circuit and also connect to the power terminals of same contactor if they are to be in separate enclosures?![]()
You do so in accordance with 725.136(D).
Chris
You do so in accordance with 725.136(D).
Chris