I need to do a calculation from head to tail on an industrial service. Is that something I could post here to make sure that I am stepping it out right? If so, tell me. I will post all the specs. Thanks
Generally incorrect. See 430.6.Another question.
When calculating motor loads, I should always use nameplate FLA when available. Correct? And 430.250 When not available?
Generally speaking, 11 through 14, if supplied by receptacle would be calculated in with receptacles. Receptacles cannot be calculated at less than 180VA per yoke....
11. Desicant Dryer 110v x 1A = 110va x 1.25 continuous = 138va
12. Manchester Tank 110v x 1A = 110va x 1.25 continuous = 138va
13. Oil filter 110v x 1A = 110va x1.25 continuous = 138va
14. Refrigerant Dryer 110v x 1A = 110va x 1.25 continous = 138va
15. Computer circuit 120V x 20 amp x 1.25 continuous = 3000va
16. PLC power supply 120V x 20 amp x 1.25 continuous = 3000va
17. Scale Monitor Circuit 120V x 20 amp x 1.25 continuous = 3000va
Well for that we're getting into interpretations, where opinions vary. First, 220.14(A) says outlet, not receptacle. Then it goes on to say for a specific appliance or other load not covered in 220.14(B) through (L)... and receptacle outlets ARE covered in (I) through (K).They sure can and I often do when I submit as-builts.
220.14(A).
I completely understand some willingly accept the practice...I got a PM from a respected member here that agrees with you, yet I will tell you the EE's and BO's here don't have a problem with me using that for rec's. Most notably I did a couple schools here (2 different counties) that had hundreds of work stations under 50 watts and my as-builts went through the EE and were approved by the bldg depts, go figure.![]()
I did, its the first 100 hp motor with the notation by it.Generally incorrect. See 430.6. I see it now, thanks.
Also, you have to calculate the largest motor at 125%. See 430.24.
I understand what you are saying, I was just calculating for a 20 amp 120 volt circuit feeding them, as the true load is not known. And it is a dedicated circuit. Which, I am taking is wrong. I need to derate the 20 amp circuit for continuous loading? Is this what you are saying?Generally speaking, 11 through 14, if supplied by receptacle would be calculated in with receptacles. Receptacles cannot be calculated at less than 180VA per yoke. They are receptacles. So just use 180va. like all receptacles, Then multiply by 1.25 for continous?
15 through 18 appear odd. Is the 20A value a loading value or the circuits' ampacity? If allowing for full loading of a receptacle circuit, you'd just use 20A (16A continuous)... and if using multiple receptacles on the circuit, you must also not be below 180VA per yoke. Also, 20A for a PLC power supply and Scale Monitor Circuit seem high.
Okay, I see it now. Typically listed first, so I didn't look further down. :ashamed1:I did, its the first 100 hp motor with the notation by it.
This is what I thought? But, code gets interpreted differently by different people. 220.14 looks black and whit to me. But then, that's my interpretation.They sure can and I often do when I submit as-builts.
220.14(A).