IMO if the awning has general lighting installed, yes. Otherwise, no.
If computers are in the office part, they are part of the office receptacles already calculated by area. When you use 220.14(K)(2), it includes all the general-use receptacles, and that value must be larger than the total number of receptacles times a value not less than 180VA each. It would be a violation if you calculated by area because you do not know the number of receptacles, and after installation end up with a value greater than calculated by area.
As for the low-amperage, 120V loads. You need to decide whether they are going to be hardwired or receptacle connected. If hardwired, you may calculate at rated current times 125% for continuous operation. If receptacle connected, just omit from listing altogether and include as general-use receptacle load... and as noted, you do not factor general-use receptacles by 125%... just make sure the VA for number of receptacles exceeds the known receptacle-connected load times 125%.
Additionally, it makes a calculation easier to follow if you do not factor each listed load as continuous, or not, but rather keep continuous and non-continuous loads (and perhaps motor loads) separate, subtotal, then factor continuous at 125% en masse. See Annex D Examples.