wmabantajr
How many cubic inches for a 4 AWG conductor? I am using a 4X7X10 box and each 1" conduit that enters it has (2)4AWG(hot) and (1)10AWG(ground) conductors in it.
A 4 AWG requires 0.0 cubic inches of volume allowance.
There are no cubic inches in the large conductor box sizing rules. The number are inches between the conduit and the enclosure walls or between the conduits. For the "conduit" size where cables are used, you use the minimum size conduit that the code would permit for the size and number of conductors that are in the cable. You do not use the size of the cable connector.Not totally clear on the 6X and 8X rule. For (2)4AWG(hot) and (1)10AWG(ground) conductors in 1" conduit would I use 6 cubic inches(6X 1" conduit)? For 4/3 MC cable would I use 4.5 cubic inches(6X 3/4" conduit)? I am using a 7"X10"X4"deep box.View attachment 7968View attachment 7969
What part of 314.16 applies to conductors #4 and larger?...
314.16 states 'Boxes and conduit bodies enclosing conductors 4 AWG or larger shall also comply with the provisions of 314.28.'
is that a receptacle installed in the side of that junction box? (if so, it's not to code)
What section is being violated?
There is nothing in 314.16 that applies to installations of conductors #4 and larger. The word "also" in the section that you quoted should not be there.the above underlined
red = text to be deleted9-39 Log #3648 NEC-P09 Final Action: Reject
(314.16)
_______________________________________________________________
Submitter: Donald A. Ganiere, Ottawa, IL
Recommendation: Revise text to read as follows:
314.16 Number of Conductors in Outlet, Device, and Junction Boxes, and Conduit Bodies.
Substantiation: There are no volumes 314.16 that let you apply the in this section to conductors #4 and larger. The only rules that apply to these larger conductors are the ones found in 314.28.
Panel Meeting Action: Reject
Panel Statement: Although there are no prescriptive requirements in this section that apply to large conductors, the parent language about sufficient size
does apply.
Number Eligible to Vote: 12
Ballot Results: Affirmative: 12
CMP 9 does not agree.
The only problem with the panel statement is that there is no way to apply the "sufficient size" wording. It is vague and unenforceable. The enforceable rules for boxes with conductors #4 and larger are found in 314.28.
can 4 AWG be spliced in conduit bodies?
I'm too lazy to look it up, but for conduit bodies, I believe there is specific language about having enough space if conductors are spliced in a conduit body.