Which can be replicated using solid-state power electronics.
Of course. But not nearly so elegantly.
Sometimes a low-tech, simple solution is the best.
Then again, if anyone could point to a 5Kw - 7.5kw VFD with an output into 0% - 100% full load that is\will:
sine wave output with THD <3%
supports Crest Factor of 3:1
support minimum Power Factor(Leading/Lagging) of 0.65 (either direction of power transfer) I'll let that one slide to .8pf
and has a regenerative front end.
And off-the-shelf would be nice - don't really want a custom built unit.
Now that would be an equally elegant solution.