Hello All,
Question on conductor of same insulation in a raceway?
1.How many #12 THW wires can fit in a 1 1/2 inch PVC sch.40 Pipe?
If you look at page.790 of nec it says 30 conductors in a 1 1/2 inch pvc sch.40 pipe, If you do it with Table 4&5 the answer is different?
Page. 717 table 5 top right of page says # 12 awg = .0181
Page. 715 Table 4 1 1/2 in. PVC pipe over 2 wires @ 40%fill is .794
If you divide .794 int .0181 the answer is 43.8 == the correct answer is 44 conductors.
is it a type o error? i think .
I also tried it with a hxxw #6 wire in a 2in emt and both Tables C.1-11 and 4,5 tables came up with the right answer.
any thoughts on this ??? thanks guys