Raceway Calculation

Status
Not open for further replies.
Location
Mass
Hello All,
Question on conductor of same insulation in a raceway?
1.How many #12 THW wires can fit in a 1 1/2 inch PVC sch.40 Pipe?

If you look at page.790 of nec it says 30 conductors in a 1 1/2 inch pvc sch.40 pipe, If you do it with Table 4&5 the answer is different?
Page. 717 table 5 top right of page says # 12 awg = .0181
Page. 715 Table 4 1 1/2 in. PVC pipe over 2 wires @ 40%fill is .794
If you divide .794 int .0181 the answer is 43.8 == the correct answer is 44 conductors.
is it a type o error? i think .
I also tried it with a hxxw #6 wire in a 2in emt and both Tables C.1-11 and 4,5 tables came up with the right answer.
any thoughts on this ??? thanks guys
 
There are errors in the wire fill tables. You have to remember that the wirefill tables are not code rules and are just there for your information.
Informative Annex C Conduit and Tubing Fill Tables for Conductors
(D) Informative Annexes. Nonmandatory information relative to the use of the NEC is provided in informative annexes. Informative annexes are not part of the enforceable requirements of the NEC, but are included for information purposes only.

 