If resistance is low enough to read without an insulation tester what more are you going to learn about the situation by using an insulation tester?
None, of course. But if it is high enough...........?
If resistance is low enough to read without an insulation tester what more are you going to learn about the situation by using an insulation tester?
OP already indicated he was certain there was a ground fault.None, of course. But if it is high enough...........?
But he was not sure how many ground faults were there and so, again, the link at post # 11 may not be depended on.OP already indicated he was certain there was a ground fault.
If you get any reading from lead to ground with an ohm meter you're done, so is the motor. There is no need to do an insulation test.Finding the status of 'degree' of grounding of phase leads of the (submersible) motor with an ohm meter may not be correct. An insulation tester is more appropriate for that.
You are also right.If you get any reading from lead to ground with an ohm meter you're done, so is the motor. There is no need to do an insulation test.