ryan_618
- Salt Lake City, Utah
The ROC can be downloaded here: http://www.nfpa.org/AboutTheCodes/AboutTheCodes.asp?docnum=70&tab=nextedition
7-12 Log #287 NEC-P07 Final Action: Accept in Principle
(338.10(B)(4)(b))
________________________________________________________________
TCC Action: The panel action on the comment placed a requirement in an Informational Note which is not permitted by the NEC Style Manual.
The Correlating Committee directs the panel action on this comment be revised as follows:
Exception: Single conductor Type USE and multi-rated USE conductors shall not be subject to the ampacity limitations of Part II of Article 340.
Submitter: Dennis Alwon, Alwon Electric Inc.
Comment on Proposal No: 7-59
Recommendation: Add Exception as follows:
(b) Exterior Installations. In addition to the provisions of this article, service entrance cable used for feeders or branch circuits, where installed as exterior wiring, shall be installed in accordance with Part I of Article 225. The cable shall be supported in accordance with 334.30. Type USE cable installed as underground feeder and branch circuit cable shall comply with Part II of Article 340.
Exception: Type USE installed as underground feeders shall not be restricted by 340.80.
Substantiation: The problem is that I don’t believe the board read my proposal correctly. Here is your comment “The submitter is referring to single conductor USE per Table 310.104(A), whereas 338.10(B)(4)(b) is referring to a USE cable assembly with a plastic covering as defined in 338.2. Single conductor USE is not limited to the ampacity in 340.80.”
338.2 does not define USE cable only as an assembly with a plastic covering as you state. It states with or without an overall covering so single conductor, triplex or quadruplex cable is relevant to this article.
The last sentence states that USE cable shall comply with Part II of article 340. USE cable can be a triplex, quad or individual cable and as written art. 340.80 states that UF shall be 60C. Thus if USE must follow part II of 340 then it must be rated at 60C when used as a feeder or branch circuit. I don’t believe this is the intent but it is how it reads. Thus with the words “excluding 340.80” USE cable would not be limited to 60C as intended. I have shown this proposal to many respected members of the electrical community and they all agreed that the board did not read the proposal or the section correctly.
I do not understand how your comment about this section only pertains to jacketed cable as it clearly states USE.
Panel Meeting Action: Accept in Principle
Add informational note to read as follows:
Informational Note. Single conductor Type USE and multi rated USE conductors are not subject to the ampacity limitations of Part II of Article 340. Requirements for single conductor USE are in Table 310.104(A).
Panel Statement: CMP-7 does not accept adding an exception to 338.10(B)(4)(b). Instead, CMP-7 adds an informational note for clarity.
Number Eligible to Vote: 14
Ballot Results: Affirmative: 14
Comment on Affirmative:
KENT, G.: Although deletion is the proper action but does not appear to have the support of the committee, this option at least offers some clarity to the wording.