Have a house without power and want to hook generator up, going to back feed panel from dryer breaker. After turning main breaker off and hooking generator up should I run a ground wire from my generator frame to the house ground rod ?
And it is cold and the house is freezing up - or already has. And, even if you had time, there isn't a switch available in the county. Just guesses.
So:
Are you connecting to the dryer breaker in the panel? Or a plug to the dryer receptacle? I'm asking because you really should put in a 4 wire feed and pull the N-G Bond from the generator. One of the 4 wires will be from the generator frame to the house EGC. If the dryer receptacle is not 4W, don't use it.
I'm guessing the generator is <10KW, 1 ph, one or two cbs, cord and plug. If it is, it should have a 4W receptacle. And it will have an N-G bond. Some of the esteemed here don't think it matters if the N-G bond is removed or not. However, as an avid DIY and engineer (industrial) I think it does.
Recommend:
4W plug and cord from the generator to the panel.
Wire directly to the panel, hots to the dryer CB, G to G, N to N.
Pull the N-G bond. If you can't find the gen book to locate the bond, don't worry about it. Just don't have any faults while you are standing on the ground and holding on to the gen frame.
Lock open the house main. Its unlikely a small gen can back feed the utility - but it is possible, It's unlikely a lineman will work the utility side with out checking - but it is possible. Put a lock on it.
As said, you need some help - this is not a bad, you are just out of your element. Take heart. If you were a DIY or worse yet - an engineer, this would have been shut down at the first post. But you are not - so you're okay.
But get some help - do it safe.
And, NO, a ground rod at the gen won't change a thing.
ice