Line side taps
Bheff
Woburn
Article 705.12(A) allows for an interconnected electric power source on the line side of the main disconnect as permitted in 230.82(6), if the power source consisted of 4 utility interactive solar inverters would it be permissable under 705.12(A) to connect the A/C output of each inverter to a panelboard with 4 branch ckt breakers, and then feed the panelboard from a line side tap at the mainservice disconnect?
That is a common practice in the industry. There is some debate as to how or if the 120% rule applies, but I know that many ASHJ's approve installations of that type.
There may be some discussion about whether there needs to be a single identified disconnect point, such as a main breaker on the sub panel in this case, or whether the spirit of the six handle rule will apply. The tap conductors have to be protected, either by a main or by the sum of the branch breakers.
Exactly, Jben.
Bheff,
If you have a smart/demanding AHJ,
and you have fuses or a breaker in the new service disco,
then you will need to size feeder conductors from the new disco to the pv brkrs for SUM of all power sources feeding it.
4 PV brkr.s PLUS any OCPD you have in the new disco........as silly as it may seem.