Looks like he will need a main in his panel anyway, so he can tap off one of the two 200 amp disconnects.
Only if the panel and feeder are less than 200 amps, tap rules still need to be met for any interior portion of the tap, outdoor tap conductors can be unlimited in length.Why?
The boss is old school, he likes to use three big horkin split bolts, load side. I like Insulation Piercing Connectors, no tape, less work.Thought about tapping one of the disconnects but I've never tapped off a fused disconnect.
Not sure how I would go about it since I suppose it would be hard to find a double lug for the fused disconnect.
There's usually a bolt on the neutral connector in the disconnect. Get a lug to fit under it and snug it up tight for the EGC.
Lately I've been eyeing Polaris connectors with three terminals. Two for the load hots and a jumper to the disconnect lug.
680.12 Maintenance Disconnecting Means
One or more means to simultaneously disconnect all ungrounded
conductors shall be provided for all utilization
equipment other than lighting.
Each means shall be readily
accessible and within sight from its equipment and shall be
located at least 1.5 m (5 ft) horizontally from the inside
walls of a pool, spa, or hot tub unless separated from the
open water by a permanently installed barrier that provides a
1.5 m (5 ft) reach path or greater. This horizontal distance is
to be measured from the water’s edge along
Even the PDB's are a last resort for me.
Generallly You can get a feeder from the inside panel if its not too far away, or, changeout the Outside
Enclosed breaker to a Main with feedthru lugs along with some distribution.
But I've been told the strut will rust/corrode at the point it enters the ground.
That's right but I was hoping he would let us know why he felt it needed a main.
Most every pool panel we have ever done is 150amp or less. If tapping from a 200 amp disc it would the wire would need to terminate at a main.
There are some main lug panels rated 150 amp, but majority of them are going to be 125 or 225.
Unless I am more confused :? than normal, or do not fully understand what is trying to be accomplished. The panel being added (tapped from the existing) needs a main.
I do not have the exact wording but this is my understanding:
240.21B(1) or 240.21B(2) the taps need to terminate in a main (either factory or back fed with a hold down)
Please correct my ignorance.:weeping:
Exactly, you no longer have a 240.21(B) described tap if the panel is rated same or higher than the feeder it is connected to.If you tap the 200a feeder to the existing panel with 200a Rated wire and a 200a Rated subpanel then its not actually a tap but an extension of the 200a Feeder. Much like would be the case with a 2 section panel with
feed thru lugs in the 1st section.