delectric123

Senior Member
Location
South Dakota
i browsed that section and at article 310.15(B) (3) its says conductors without spacing longer than 24 in. Does that apply to single condutors in a raceway? Am i interpreting this right?
 

delectric123

Senior Member
Location
South Dakota
Thank you, all, this is a very helpful forum. does the code have any derating requirements on bundled conductors in Industrial Control Panel Wiring? like conductors in a wire ductt? besides common sense
 

Smart $

Esteemed Member
Location
Ohio
Thank you, all, this is a very helpful forum. does the code have any derating requirements on bundled conductors in Industrial Control Panel Wiring? like conductors in a wire ductt? besides common sense
310.15(B)(3)(a) applies to ICP's that are not listed equipment (or a component thereof)...
where single conductors or multiconductor cables are installed without maintaining spacing for a continuous length longer than 600 mm (24 in.) and are not installed in raceways, ...
 

kwired

Electron manager
Location
NE Nebraska
There is this sentence embedded within 310.15(B)(3):

Where conductors of different systems, as provided in 300.3, are installed in a common raceway or cable, the adjustment factors shown in Table 310.15(B)(3)(a) shall apply only to the number of power and lighting conductors (Articles 210, 215, 220, and 230).