Bjenks
- East Coast of FL
I am doing a generator replacement and believe there is a problem with the existing wiring, but wanted to make sure I didn't miss something or over react. Basically, the emergency power from the generator has all three phases and the EGC going to the ATS, but the Neutral goes right into the Emergency Panel and bypasses the ATS. The Normal source Has a Shunt Trip Service Disconnect Breaker fed from a gutter that has the service Neutral tapped with one going to an isolates neutral lug of the disconnect and the other going to the Emergency Panel. So the Emergency Panel has two large Neutral conductors on it, from the generator and from the service. Further the service disconnect neutral is not bonded to the frame and stops at that point with no EGC going to the ATS. So it looks like they bypassed the ATS with the neutral all together. I am going to require the following items to be fixed:
1) the Service Disconnect must have a N-G bond and continue on to the ATS with an isolated Neutral and EGC.
2) Remove the Neutral Service Tap to the Emergency Panel.
3) Remove the Neutral Generator Conductor from the Emergency Panel and re-feed it to the ATS Neutral Lug.
4) Re-Circuit the Emergency Panel so the Only Neutral supplying it is the ATS.
So while I know this will be a cleaner install and the service disconnect must be fixed I am wondering if the bypassing of the neutral to the ATS was allowed? Every ATS installation drawing I have seen shows the Neutral, but it also shows the switched neutral as an option. BTW the generator is acting as a separately derived source.