I use Wago's and Ideal's all the time with great results. No difference between these and non bolt in circuit breakers.
With that logic would you also say that push in receptacle slots were reliable. I see the Wago's as having the same function as a push in the back receptacle. It relies on tension to hold the wire not screws.
Anyone seen a failed Wago? I have not
Anyone seen a failed push termination on a device? I have
How about you?
There are similarities, there are also differences.
When you make up a receptacle, you insert the conductors into the termination, then you push against that termination when mounting the receptacle in the box. Who knows if there is any pressure in the wrong direction, or at the wrong point compromising that connection. With the Wago (or similar) product, you insert the conductor(s) in the device and then you usually bend the conductors instead of pushing the device to position it.
I've seen 1 failed wago in all the years I've been using them. This one was on a residential circuit where they were running 2 1500 watt space heaters on a circuit, connected to a Zinsco breaker that never tripped (imagine that). And I suspect that the wago wasn't properly installed, but can't be sure.
We use them extensively.
@electricguy61
Could you please tell me the WAGO product you are using? Is it the WAGO Series 773?
Thanks
How about you?
Those are the ones. We stock the 4 & 8 wire on the trucks.