Thanks to all of you. Let me re-clarify some things. This is a cord and plug connected portable heater with a built in blower that is UL listed, including a 15 amp cord cap. It is relatively new. Nameplate rating is 1500 W@120V. That is only info on nameplate. I should have stated that there are no 20 amp ckts available for plugs. only 15 amp. I,m assuming that if there were a 20 amp ckt , then there would be no issue since (2400x80%=1920W or 16 amps, and plugging this appliance into any plug on a 20 amp ckt would make this code compliant. That is not the case. In addition, this house was built in 1940 / knob and tube wiring. In addition, tenant is using a ground adapter since there is no ground. And this heater has a ground pin on the cord cap. I simply stated to the homeowner that this appliance requires a dedicated ckt because of the fact that 210.23 (A) (1) requires it bases on this particular situation. I do have a couple questions regarding replies to this thread. More than anything else, I want to be sure that I am understanding the codes intent here. To Mgraw,s reply: This is a 15 amp cord cap. My understanding of 210.23 (A) (1) is that this heater would be a code violation to use in this case because of the 1500 W rating on nameplate, and due to the fact that there are no 20 amp ckts. available. To iwire: Isn't anything over 12 amps a violation on a 15 amp ckt (1800x80%=1440W. or 12 amps regarding this particular discussion? To Infinity: Where in the code does it state that this heater needs to be considered a continuous load? I understand the calculation. And am sure that this heater would be plugged in for 3 hours or more on occasion, and if I ran a ckt, it would be a 20 amp ckt. Just some info about this call. Property owner called me to check out the situation at property address. Tenant stated that the cord was really warm at plug location. I verified that it was and assessed the situation. I stated that this appliance required a dedicated ckt., in this situation. Tenant stated that the owner should be responsible for this. Just so everyone understands, I don't care who pays. My #1 priority is Life and property protection for all concerned. I have seen consistent problems with these portable heaters over the years. Particularly in rental properties. Simply because of the fact that many people are just unaware of the potential dangers involved. And I overshoot when it comes to safety. I always try to reduce the load on the original house wiring whenever I can, including adding grounds where possible. I just want to be sure that my statement to tenant is correct in this situation. Thanks again for everyones imput. I,m always learning here.