Thanks kwired. So this portable heater would not meet the definition as defined in 210.23(A)(1)? And 210.21(B)(2) specifically states "shall not supply a total cord-and-plug- connected load in excess of the maximum specified in Table 210.21(B)(2)" Also, Article 90.5 clearly prohibits, or requires an action by the words "shall" or "shall not" An interesting note here: I will reference Mike Holts " Understanding the NEC, Volume 1, Articles 90-450. Please see pg.81 which shows a picture of my exact situation. Permissible loads for cord-and-plug-connected equipment not fastened in place section 210.23(A)(1). The only difference is that in my case, it is a portable electric heater instead of a drill press. If these code sections that I have cited don,t apply to my situation, then what do they apply to? I believe that as an electrician, I have an obligation to know what i,m talking about. I looked up this info, and told tenant that it would be an NEC violation to plug this heater in the 15 amp duplex receptacle in this area that is fed with 14 gauge wire, and on a 15 amp ckt which also has other receptacles and also some lights on the same ckt as well. If I,m wrong, please just help me understand why I am misinterpreting the code on this issue so that I can be a better informed electrician at the end of the day. Thanks again.