Annex-D Problem D8
Motor Circuit Conductors, Overload Protection, and Short-Circuit and Ground-Fault Protection
The entire problem, with solution, is included in the attached Word.doc file.
This problem includes three(3) motors
1 squirrel cage motor
2 wound rotor motors
I'm wondering why the load (current) for the wound rotor secondary circuit is NOT included in the Feeder Short-Circuit and Ground-Fault Protection calculation.
In other words...the feeder calculatoin for the three-motors is provided with the problem. But the load for the wound rotor secondary is left out. Why ? Any guess ?
Because wound rotor/secondary is powered by induction, not by it's own power source, so to speak ?
Thanks, ToolHound
	
		
			
		
		
	
				
			Motor Circuit Conductors, Overload Protection, and Short-Circuit and Ground-Fault Protection
The entire problem, with solution, is included in the attached Word.doc file.
This problem includes three(3) motors
1 squirrel cage motor
2 wound rotor motors
I'm wondering why the load (current) for the wound rotor secondary circuit is NOT included in the Feeder Short-Circuit and Ground-Fault Protection calculation.
In other words...the feeder calculatoin for the three-motors is provided with the problem. But the load for the wound rotor secondary is left out. Why ? Any guess ?
Because wound rotor/secondary is powered by induction, not by it's own power source, so to speak ?
Thanks, ToolHound