Jumper. Thanks.
I looked at what you nicely wrote above.
The part in red...I am wondering about that.
One question about the '81 A' , in red above...one question
about that would be...would that '81 A' need to be included in the 'feeder protection calculation' ? ( i.e., the feeder protection calculation laid out in the solution provided in the book )?
Thanks. ToolHound
No. That is the minimum conductor ampacity of the wires to the motor.
Feeder OCPD sizing is largest individual motor OCPD + FLC of all other motors..
From the example in question.
Feeder Short-Circuit and Ground-Fault Protection
The rating of the feeder protective device is based on the sum of the
largest branch-circuit protective device (example is 110 A) plus the sum of
the full-load currents of the other motors, or 110 A + 40 A + 40 A = 190
A. The nearest standard fuse that does not exceed this value is 175 A [see
240.6 and 430.62(A)].