Dustin Foelber
Senior Member
We have an condo rehab project where they are replacing the condensing units for HVAC. To these units we have single phase 240 10awg. Units min circuit ampacity is 22 but the maximum overcurrent protection is 35. The inspector is requesting us to change the feeder to #8 and install 35Amp breakers. My question is does the max OCP need to be followed or can your drop it down. Also is it NEC compliant to have 10 AWG on 2pole 30s feeding the unit yet 35 amp fuses protecting? I appreciate any input.