flatlander
- Diamond bar, CA , Tempe AZ
Hi all , Been some time since my last post. I felt I need to post on this item.
I had a residential customers underground feed go out the other day. It seems that one of the hots failed clear. The POCO was contacted and arrived in reasonable time. I thought they were going to refeed around the break but instead they just fed the working hot to both phases of the panel and left. They told the customer to just reduce what they use.
I called the troubleman to inquire and they told me that " yup that is what they do all the time"
I suggested to them that they need to be aware of multi-wire circuits. The troubleman did not know what it was. I said a 3 wire circuit , two hots and Neutral. I further said two 15 amp circuits and a single Neutral. The neutral carries only the unbalanced load. I got the HUH. and so ? Nothing wring with that he said. I said however the way you just connected the house if one of those circuits have 12 amps on each breaker with the shared neutral you will have 24 amps on a 15 amp wire. He say's no you won't each circuit has their own neutral. I said no not if you have a 3 wire ( multi- wire circuit)
After much time and frustration the Troubleman says " that is stupid" " the house is wired wrong" I said it is perfectly correct. it's been done that way for decades.
He replies with that is wrong and it ain't my problem. I tried and tried but I could not get the point across.
Don't they teach these guy's basic electrical.