A convenience outlet under the NEC is called a general-purpose receptacle. Such a receptacle has no specific load.Is there a place in the NEC that defines PCs as convenience outlets? I think that since PCs are on 24 hours a day in most commercial offices they wouldn't be considered convenience for the purposes of demand calcs. For a 100,000 VA of PCs a demand factor or not can make a big difference.
That's sort of the point I was trying to make in my system only drawing 250W. I built my computer so it doesn't have a nameplate, but I know it has a 1200W power supply. AFAIK, the nameplate rating on a manufacturer built computer is likely to indicate the power supply rating, as that will be the worst-case current.Good question about the load. I guess the only way to know for sure is see the current draw off of the PC nameplate.
But they are not expected to be running at their maximum current for longer than 3 hours. So they don't meet the definition of a "continuous load."PCs also remain on all day and should be continuous loads since they are on longer than 3 hours?
I wouldn't call a PC an appliance, but that's moot as it is a load. There is no fault in your premise. IMO, this is an area of design decision.220.44 demand factor for receptacles apply only to 220.14 (H) & (I). Section 220.14 (A) Specific Appliances or Loads says an outlet for a specific appliance OR other load not covered in 220.14(B) through (L) shall be calculated on the appliance or load served. A PC is a specific appliance so wouldn't this fall into 220.14 (A)? Demand factor isn't applied to 220.14(A) so PCs wouldn't get a demand factor. Is this correct?