tonype
- New Jersey
What about 230.70(a)(1)?
Actually, assuming the fire rating is maintained on the internal wall, I believe it is legal.
230.6 Conductors Considered Outside the Building.
Conductors shall be considered outside of a building or
other structure under any of the following conditions:
(2) Where installed within a building or other structure in a
raceway that is encased in concrete or brick not less
than 50 mm (2 in.) thick
Okay what about it? OP never said anything about the disconnecting means changing.
The disconnecting means in no longer at the point nearest the service entrance. Unless what you put in your edit above applies, which I am not sure of.Okay what about it? OP never said anything about the disconnecting means changing.
I do not believe they are encased in brick, just hidden.
In my area that is a fail, other areas maybe not.
The length of SECs inside the building has been increased, that would be a 230.70 issue.
Owner recently decided to install an 8" decorative block to outside of an industrial building - underlying walls are also masonry block and brick). Service entrance conduit is now buried between the layers. Is this legit?
Reads like encased to me. SECs between 2 layers of CMUs/brick/block/etc.
Between is not encased.
So what is your definition of encased?Between is not encased.
Disagree here.Maybe.............
: to enclose in or as if in a case
http://www.merriam-webster.com/dictionary/encase
enclose:
Surround or close off on all sides.
According to Merriam Webster, it means "to surround" - with a synonym of "pen in" and "corral".
Are you thinking of embed, which M-W defines as "enclose closely".
Of course neither of our opinions really maters, it is entirely up to the AHJ.![]()
I don't disagree with any of the points you have brought up here. I still think most AHJ's will accept in principle considering this outside the building as long as the masonry wall between the raceway and the building interior is intact.I also would be very surprised if the top of this slot is masonry, most likely wood wood with metal flashing on top.
I wonder if there is an LB at the bottom that got covered up.
Good question. Or maybe a meter cabinet is now flush or semi flush.
But does it turn to get "inside" with a sweep or an LB?Everything else (meters, service equipment, etc) is inside.