Just had to throw that one on the fireJust curious, does the DB cable have an overiszed EGC?
Could be, take a look at 250.122(B).Now that you jogged my memory It needs to be? It also needs to be when you parallel conductors?
ptonsparky made a good point. It all depends on where the first 100A breaker is, i.e. you can put 4/0AL on a 200A breaker and run it ten feet on up to ten miles or more and not have to use a larger EGC. Put the same wire under a 100A breaker or less and you need to upsize the EGC.There seems to be a other opinions though?
Make sense? Of course not.
What's important is- Why did you upsize to 4/0? What is the connected load? If you need 100A at a great distance from the source then voltage drop is a real concern and the EGC should be upsized.
It is only with 15, 20 & 30 amp circuits that 250.122(B) causes real heartache.
Once you get above those sizes things make much more sense.
It gets better but doesn't go away. Take a 40 amp circuit and increase conductors and you are supposed to increase EGC by same proportion, yet if same ungrounded conductors were part of a 60 amp circuit the EGC could easily be smaller than what may required by the 40 amp circuit.
Did I say it went away?
Do you think I am unaware of the rules?
It just seems every time you quote me it is to correct me over things I did not say
Did it ever occur to you that maybe I was just adding my own $.02 and was talking to the entire forum and not just you?