francis.key19
- frederick, md
Hi,
I have a contractor who is running paralell feeders (3/0) for us on site. The service is for a 600HP drive, 3 phase, 4 wire. The route is to use the first 120ft of an existing ladder tray, then the remaining 30ft will be 4" conduits. They ran 2 (two) 4" conduits, instead of 3. Several questions concerning this installation. Contractors said the installation is proper and followed codes.
1. Should there have been 3 conduits where in each one, we should have A,B,C, N and Ground conductors?
2. I only see one ground 3/0. Contractors said only need one since most the distance are in the tray. What if there is a short in the conduit?
3. Since the cables will be in open air on tray then in conduits, how should the conductors be derated?
Lastly, this contractor took 7 days for the installation with 3 people. This seems a little bit much for this work. The tray is existing, and conduits are ran in open area 16ft elevation. Any idea how long this work should typically take?
Thanks.
Francis.
Thanks.
Francis.