Service for 4-unit multi-family condo building

Status
Not open for further replies.

lmcgill

Member
Wondering if the anyone knows of any Code that would NOT allow routing the electrical service from a meter bank through one tenant's basement or crawl space into another tenant's basement or crawl space and up into a panel. Any help would be greatly appreciated. Thanks,
 

Smart $

Esteemed Member
Location
Ohio
Wondering if the anyone knows of any Code that would NOT allow routing the electrical service from a meter bank through one tenant's basement or crawl space into another tenant's basement or crawl space and up into a panel. Any help would be greatly appreciated. Thanks,
Where's the service disconnects located? They have to be outside or inside nearest the point of entrance... and running service conductors through a basement or crawl space means the disconnect does not qualify as either... 230.70(A)(1).
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
Wondering if the anyone knows of any Code that would NOT allow routing the electrical service from a meter bank through one tenant's basement or crawl space into another tenant's basement or crawl space and up into a panel. Any help would be greatly appreciated. Thanks,

I get the sense that you are referring to feeders as opposed to service conductors, yes? If feeders there is no NEC violation but there may be building code issues-check with the AHJ.
 