I haven't found if it is or isn't authorized to stub out uf cable for an outdoor receptacle on a single family dwelling, without running the stub out through the wall in some sort of conduit, flex, etc. The uf cable would be ran through the OSB siding, tyvek, and then be placed in a box within a brick wall as usual.
Under 340.12 uses not permitted, it says that uf cable is not permitted "embedded in poured cement, concrete, or aggregate.
The exterior of the house will be brick, but that doesn't mean the uf cable would be in "poured cement".
UF cable is permitted in wet, dry, or corrosive location, but that isn't really the issue. I believe the intention of the conduit sleeve was to protect the wire from damage. So we get into the subject of "where subject to physical damage?"
Is there a code reference I am missing on this subject?