sleaving NM cable thru conduit

Status
Not open for further replies.
is it permissible to sleave nm cable(S) thru conduit?
i am getting mixed info from my co-workers with no NEC reference
an answer with an article referance would be greatly appreciated
-cheers
 
Yes its ok, but for indoor use only (NM cable is not allowed in wet or damp locations). Conduit fill must be considered. Heres one that makes it clear: NEC 334.15 (B) Note: I’m rusty
 
Last edited:
NM through conduit

NM through conduit

The code states that when transferring from one wiring method to another you must use a J Box unless a UL approved fitting is used Check out Bridgeport Fittings # 280-DC This will allow for nm to 1/2 EMT
 