a question......
i want to put five 3 hp motors on the same motor starter....
480 volt 3 phase motors driving exhaust fans in a factory.
so, i go with 125% of the full load current of one motor plus
the sum of all the motors is my understanding....
so if i size the contractor for that ampacity, the running overcurrent
protection will still be in place for each individual motor, as any one
of them pulling excessive current flow will interrupt the starter the
same as if it was only a single motor, with appropriately sized heaters.
am i correct in this belief?
my other question is, i have two ways to run this... i can go with
pipe on the roof, teeing off and feeding fused disconnects for
each motor, or running it underneath the roof of this tilt up,
off a lift, with EMT. the over the roof method most likely will be
GRC. i have to check with the AHJ what their local rules are.
i also have to deal with derating the conductors if they are
close to the roof, which they would be..
the plus side is it would go a lot faster putting it in on the roof,
on blocks, than running underneath off a scissor lift.
the total run is 250', so voltage drop would require #8's for
the voltage drop.
so, what 'choo guys think? over the roof or under the lid on a
lift?
the other thought is that MC cable in #8 would go up pretty damn
fast, but isn't gonna get a photo shoot for beauty.
how would you do it?
i want to put five 3 hp motors on the same motor starter....
480 volt 3 phase motors driving exhaust fans in a factory.
so, i go with 125% of the full load current of one motor plus
the sum of all the motors is my understanding....
so if i size the contractor for that ampacity, the running overcurrent
protection will still be in place for each individual motor, as any one
of them pulling excessive current flow will interrupt the starter the
same as if it was only a single motor, with appropriately sized heaters.
am i correct in this belief?
my other question is, i have two ways to run this... i can go with
pipe on the roof, teeing off and feeding fused disconnects for
each motor, or running it underneath the roof of this tilt up,
off a lift, with EMT. the over the roof method most likely will be
GRC. i have to check with the AHJ what their local rules are.
i also have to deal with derating the conductors if they are
close to the roof, which they would be..
the plus side is it would go a lot faster putting it in on the roof,
on blocks, than running underneath off a scissor lift.
the total run is 250', so voltage drop would require #8's for
the voltage drop.
so, what 'choo guys think? over the roof or under the lid on a
lift?
the other thought is that MC cable in #8 would go up pretty damn
fast, but isn't gonna get a photo shoot for beauty.
how would you do it?