I know I am not on your Christmas card list but none the less I will toss this out.
Are you ready to do all that?
Here is my thought and it is radical.
Purchase five correctly sized enclosed magnetic motor starters a piece of wireway and put them together. Don't forget these are motor controllers and require a disconnecting means in sight of them.
That being the case it usually makes sense to place the motor starters in sight of the panel they are supplied from and run each circuit from there to the motors. 250' is not long considering you could use 12 or likely even 14 AWG for them.
Also from a maintenance and service perspective having the starters in some odd place just to make the installation easier stinks.
As far as MC or pipe ........ are you in business to make money or make art?
I would let the customer decide that, provide prices for both ways and let them decide if it is 'cheezy' or not.
"This thread has more than 10 replies. Click here to review the whole thread."
geeze... i can feel the lurve from here.....
i'm not ready to do "all that". it was about all i could do to wade thru the replies... :dunce:
i was trying to figure a way not to have to run 1,000' of 1/2" emt for five little motors.
your thought about 5 starters in individual enclosures was my first choice.
and the one i'd bid with, before i got busy trying to be creative
and painting myself into a corner. thank you for taking the time to respond.
each fan draws 4.8 amps... so even allowing for derating for multiple wires
in the conduit, #12 will still be ample, and the voltage drop on 480 will be
1.36% with #12 wire, so that isn't a problem, and the fugly truth is, doing
it your way will need *far less* pipe and wire than doing it my way.
the bestest way to do it would be to drop j boxes with 1/2" emt down thru
the sleeves on the fans, and connect it with 1" emt, and T condulets. put a
pull string in the pipe, and start at the end, and work my way backwards,
pulling a set for each fan. pull 10' out of the t, and shove it up to the roof.
put the cover on the t. move on.
add another pair of wires for the T stat, and put a t and run down a column
wherever the customer wants the t stat. use a 110 volt t stat, and thhn wire
for the t stat leads.
so, i've got one 1" emt run feeding five motors, five motor starters in individual
cans, one 1" emt going to the switchgear with some #8's in it to feed the starters,
a T stat on a column with a pair of wires going to it. the dots are connected, make
up the stuff, and i'm done.
the area the job is at..... it's bell gardens..... for those of you who know LA, it's
not the best area to work in.... but... it's better than compton... :happyyes:
at least i don't have to bring a helper to provide covering fire while i go to the
van for material...