Doc777
- Sioux Falls, SD
The AFCI protecting the under cabinet microwave is tripping during the night while not in use. New home is 7 years old, 1100W microwave is also 7 years old. While unplugging the microwave from the dedicated 15A duplex receptacle (on a 20A breaker and 12/2 single run to the outlet) I discovered the receptacle was lightly scorched and the heavy rubber cord end right at the hot & Neutral prongs was slightly melted. Obviously there was/is heat buildup at the plug/receptacle junction. At first I attributed this to items in the cupboard where the outlet is located as pushing the cord end around in the receptacle. No other problems are present with the microwave.
After inspecting the circuit wires and finding no evidence of damage, I replaced the Duplex receptacle with a 20A dedicated single receptacle, and replaced the power cord on the microwave (it can not be hard wired), and made sure items in the cupboard did not effect the cord end. For extra protection I installed a new Siemens 20A AFCI breaker into the panel at location #4 with other 20A non AFCI loads around it. No other breaker tripping is occurring in the panel.
The AFCI will trip during the night (It sometimes will go 2 nights before tripping) while the family is asleep and the unit is not in use other than a clock display. It never trips during use. The LED trip lights on the breaker indicate an arc fault to ground. I'm tempted to uninstall the AFCI breaker in favor of a standard breaker but am concerned that there may be a an actual fire causing issue with this.
Any ideas on whats going on here?