hi
I want to install a contractor(ignition source) inside an dust tight enclosure(electrical panel) in C2D2 group G.
but do I need to add ex proof seal to the enclosure?also Can I use NEMA 4 enclosure as dust tight enclosure???
I have often wanted to install a contractor in an enclosure as well.![]()
hi
Explosion-proof seals are never required for a Class II area. Some type of seal is required to prevent the dust from entering the enclosure. I have often seen the standard Class I seals filed with duct seal used for this application.
OK,according to nec codeI have often wanted to install a contractor in an enclosure as well.
NEMA standards no longer really apply for enclosures. They have been taken over by UL. Many (UL) type 4 enclosures are also rated as type 12. Type 12 is dust tight, type 4 is not.
You need to re-read Section 502.15 VERY carefully. Dusttight and dust-ignitonproof are not the same thing. Only dust-ignitionproof (Type 9) is ever required to be sealed at all ? and not always.
Section501.15 (1) through (4) lists the acceptable ways of ?sealing? dust-ignitionproof enclosures.
Unlike IEC IP designations, a higher number does not necessarily mean a higher degree of protection. I?ve told you before ? quit trying to apply IEC concepts. EDIT ADD: I HATE TRYING TO USE THIS EDITOR
Some AHJs have an issue with any of the foam products unless there is some documentation that says the foam will not damage the conductor insulation.Perhaps you meant 502.15?
I have seen people use expanding foam. That seems like it ought to be compliant with method (1).
What the heck does (4) mean?
Yes - I meant 502.15 :ashamed1: I'm having so much trouble with the editor. I lost track.Perhaps you meant 502.15?
Basically, it means that the "unclassified" end, whether open or terminating in an enclosure that doesn't need to be sealed itself, must be below the dust-ignitionproof enclosure. Technically, the total length still needs to be not less than 10' and the vertical portion not less than 5'....
It doesn't; it's a matter of practicality. Unlike cables [Section 502.10(B)(1)(6)],there is no provision for terminating a raceway in a Class II location except in an enclosure, but it isn't always necessary to terminate in an enclosure in an unclassified location; i.e., there are no specified "boundary" requirements, just those between dust-ignitionproof and non-dust-ignitionproof locationsI don't recall it actually says the other end of the raceway has to be in an unclassified area.
Good for you! You have done your homework and discovered that the contactor enclosure is not required to be dust-ignitionproof in Class II, Division 2 [502.115(B)] in which case no seal is required at all. However, unless you are attempting to use with "nonincendive field wiring" [502.10(B)(3)](which I don't recommend for you) all wiring methods and enclosures inside the Class II, Division 2 location must essentially be dusttight.[502.10(B)]OK.in C2D2, dust tight enclosure is acceptable for relays(sparks,arcs) and Section502.15 (1) through (4) lists the acceptable ways of ?sealing? dust-ignitionproof enclosures.
But I m tryng to find a good way to make effective seal like Section501.15 (1) for the openings in the box.
so ,do you think the foam ,silicon or fiber(that used with sealing compound) will be good for sealing ???:blink:
also , can I use non sparking fan in C2D2??? Because I read "" 502.125(B) Motors and Generators""the motor shall be totally enclosed nonventilated, but I did not understand the concept!!!:?:?
I am not aware of seals made for Class II installations. I have also seen duct seal used in conduit bodies for that purpose and the Article permits a 10' of horizontal conduit or 5' of vertical conduit running out of the bottom of the enclosure to act as the required seal.