Hello all
I brought several AC circs out a throughout a home.
I was originally going to run twenty amps per.
The windows are small and the current ACs are small
120v 4.8 amps each. So I ran fifteen amp circs instead. Home runs to the panel.
To save on AFCI breakers any issues with running two
On one circ ? Does 125% plus 100% apply here?
4.8x1.25 = 6 plus 4.8 = 10.8.
Or is there some article that says it has to be rated 350%
And if in jersey 695% ???
Thank you.