Shouldn't matter to the hazardous location rating, and should run cooler than the incandescent, but as golddigger mentions enclosed CFL's do have heat issues that effect life of the CFL.
Just to get it clear in my mind, you are using "breathe" to refer to enough air flow to prevent a pressure change from expansion, etc., but not free air flow as would be important for heat transfer?BTW luminaires "breathe" just like any other enclosure in Class I applications. Well, Zones recognize "restricted breathing" for certain 'Type "n"' protection techniques, but that isn't under discussion here - and they still "breathe".
Yes, basically. All explosionproof enclosures permit air flow during normal air pressure/temperature changes. It's one of the reasons water condensate may form. It is expected that ignitable vapors will also collect in them and air passages are expected to create a "flame-path" that cools the internal ignited materials to below the AIT of external gases/vapors. "Heat transfer" is typically accomplished by radiation.Just to get it clear in my mind, you are using "breathe" to refer to enough air flow to prevent a pressure change from expansion, etc., but not free air flow as would be important for heat transfer?...