3 Phase Current Flow
ggunn
Austin, TX, USA
The fundamental understanding here is that the neutral is a balancing leg, similar to the current carrying conductors in AC. So, one hot leg cannot conduct current by itself without a "pressure relief valve" so to speak. Within each 1/60 of a second, the amount of current in protons flowing to the load will symbiotically produce the same amount of electrons flowing back to the source.
Protons do not flow. Implicit positive charges (holes) flow in semiconductors in the opposite direction from electrons, but a hole is just where an electron could be but isn't.
Julius Right
Electrical Engineer Power Station Physical Design Retired
The current entering one phase will return through the other two phases. If you don?t have a neutral the sum of all three currents entering the receiver [wye or delta] will be zero.
Let say current per phase[R,Y,B] is IR=I*cos(w.t)+jsin(w.t) ; IY=I*cos(w.t-2.PI/3)+jsin(w.t-2.PI/3) ; IB=I*cos(w.t-4.PI/3)+jsin(w.t-4.PI/3)
If t=0 IR=I; IY=I.[cos(-2.PI/3)+j.sin(-2.PI/3)] ; IB=I.[cos(-4.PI/3)+j.sin(-4.PI/3)]
IR=I,IY=I.(-0.5-j.0.866),IB=I.(-0.5+J.0.866) then IR+IY+IB=0 or IR=-(IY+IB)
ggunn
Austin, TX, USA
Not in metallic conductors, but they can (like hydrons) in other materials.
Yes, in aqueous acid solutions, protons (hydrogen ions) do indeed flow. I don't think that is what he was talking about, though.
mivey
And he wasn't talking about semiconductors either so the broader comparison sticks.
Charge flow with moving positive particles is not just limited to batteries. You can also have it in common things like electrolytic capacitors, mercury switches, fuel cell membranes, gas discharge elements (both natural like sparks and lightning as well as man-made like neon & fluorescent tubes & arc lamps), as well as pure nature like organisms (yes, thine own self), earth, ocean, and sky.
mivey
But only in very limited circumstances (e.g. hydronium) are those particles protons. Other positive ions, yes.
Correct. And in either circumstance they are more than implicit positive charges but actual moving positive charge carriers.
Sahib
India
Electrons are light, dynamic and fast moving particles, compared to which heavy positive ions are too slow. I think due to this that battery charging such as for a cell phone takes a long time to complete.
topgone
You say it takes a lont time to charge your cell phone? That would be like ancient fact with this development!:D
GoldDigger
Placerville, CA, USA
Retired PV System Designer
An interesting way of looking at things.
The reason that batteries are slow to charge is that heat is dissipated in the batteries as a result of charging inefficiencies.
To some extent this is because the ions involved in the chemical reactions have limited mobility.
This is one reason that a simple capacitor where only elections are moving on each electrode can support higher charge and discharge rates.
No inefficient chemical reactions are involved.
But I would have thought to attribute it to the lightness of the electrons. It is more their mobility within the metal or semiconductor than their mass that is important.
Tapatalk...
mivey
Fast or slow, the ions in the battery have to keep up with the electrons in the wire or there is going to be a KCL problem.
FWIW, only the surface electrons on a metallic conductor move near light speed when a electric field is applied. They shift and create net surface charges that lead to the movement of the electrons inside the conductor. This internal movement is relatively slow.
The light interference at the retinal receptors causes a dynamic slowdown in the charge rate similar to what happens in di-hydrogen monoxide thermal elevation.
Sahib
India
Yes, but think this way: the ions initiate the current flow and not the electrons in this case. If the electric conduction is all by electrons, current flow would be faster, higher current, higher rate of charging and so shorter charging period.
You are forgetting Einstein again: when the speed of a particle with a rest mass approaches the speed of light, its mass tends to infinity. The conductor would simply break off the circuit due to huge weight gain if its surface electrons try to behave that way.
Besoeker
UK
Actually, in terms of moving current along a conductor, they move astonishingly slowly.
I did some sample calculations a while back and I know that copying and pasting from a spreadsheet doesn't format well but here goes anyway:
I 1000 A
PI 3.142
r 18 mm
A 1017.87602 mm^2
Q 8.5E+19 per mm^3
e 1.6E-19
v 0.072238082 mm/sec
Worked better than I expected...:)
This for copper. Note the v. And the units.
I'm sure, since you are an erudite chappie, you will know of the train and tunnel analogy so you will doubtless excuse my indolence in not typing it out here.
Smart $
Esteemed Member
Ohio
I 1000 A
PI 3.142
r 18 mm
A 1017.87602 mm^2
Q 8.5E+19 per mm^3
e 1.6E-19
In imperial units...
1,000A
2,000kcmil copper conductor
0.00284402in/sec
Sahib
India
Bes:
If you apply the same voltage which caused electrons current flow of 1000A in your last post to cause a current of protons, the protons current flow will be lesser due to lower mobility or lower drift velocity of protons. Please repeat your calculation for a current flow of entirely of protons and see for yourself how less the protons drift velocity will be for the same voltage applied.
Smart $
Esteemed Member
Ohio
Bes:
Didn't check his numbers, but I assume his calculation is based on one electric charge per atom and atom size. The result is the average net flow rate. Additionally we're talking about copper. Proton drift is negligible, right?
Sahib
India
Smart $:
When the current is by flow of ions, the current may be lesser than when the current is by electrons for the same voltage. I am trying to make that point.
Besoeker
UK
Smart $:
My calculation is simply for current. No other extraneous factors are involved. Your comment about the voltage is thus irrelevant.