The wording is fuzzy to me in 310.15(a)2's exception. The debate in class, taught by a state inspector, was whether the 10% is 10% of the circuit length, or 10% of the portion of the circuit which is rated at the higher ampacity. Common wisdom around here declares that it is 10% of the total circuit length, but Mike Holt's video and the way I read it seem to indicate the latter.
Example of a 100' run, a section of which runs along a rooftop. I do not have to adjust the conductor's ampacity if it runs through this hotter section no longer than (a) 10', or (b) 9'?
I've been searching the web and the forums for a while but have not found this question addressed. Apologies if I missed it. Thank you.
Example of a 100' run, a section of which runs along a rooftop. I do not have to adjust the conductor's ampacity if it runs through this hotter section no longer than (a) 10', or (b) 9'?
I've been searching the web and the forums for a while but have not found this question addressed. Apologies if I missed it. Thank you.