Here we go, The NEC commentary does not coincide with the IAEI comments in the analysis of Changes. Both are NFPA associated. Whom is correct?
210.8 Ground-Fault Circuit-Interrupter Protection for Personnel
Ground -fault circuit-interrupter protection for personnel shall be provided as required in 210.8(A) through (D). The groundfault circuit-interrupter shall be installed in a readily accessible location.
(A) Dwelling Units. All 125-volt, single-phase, 15- and 20-ampere recept acles installed in the locations specified in 210.8(A)(1) through (10) shall have ground-fault circuitinterrupter protection for personnel. (6) Kitchens ? where receptacles are installed to serve the countertop surfaces
2014 NEC Handbook Code Commentary; Receptacles installed for disposals, dishwashers, and trash compactors are not required to be protected by GFCIs. A receptacle(s) installed behind a refrigerator is installed to supply that appliance, not the countertop, and is not covered by this GFCI requirement.
(7) Sinks ? where receptacles are installed within 1.8 m (6 ft) of the outside edge of the sink
2014 NEC Handbook Code Commentary; Sinks in kitchens are not the only sinks where a ground-fault shock hazard exists; therefore, this requirement covers all other sinks in a dwelling. any 125-V, 15- or 20-A receptacle installed within 6 feet of a sink located in other than a kitchen is also required to be GFCI protected.
2014 Analysis of Changes; A revision to 210.8(A)(7) for GFCI protection for dwelling unit sinks removes the words ?located in areas other than kitchens? to require GFCI protection for all 125-volt, single-phase, 15- and 20-ampere receptacles installed within 1.8 m (6 ft) of the outside edge of dwelling unit sinks (including kitchen sinks).
For the 2011 NEC, the title was simplified to just ?Sinks,? but excluded kitchen sinks as the GFCI provisions for kitchen sinks was covered at 210.8(A)(6) and this list item only required GFCI protection for receptacles that served a kitchen countertop and did not intend GFCI protection for such things as a receptacle under the kitchen sink for a garbage disposal, even though that garbage disposal receptacle might be within 1.8 m (6 ft) of the outside edge of dwelling unit kitchen sink. Now, for the 2014 NEC, this provision was expanded to all dwelling unit sinks (including the kitchen).
As an example, GFCIprotection will now be required for a receptacle outlet that supplies the
kitchen disposal under the kitchen sink.
210.8 Ground-Fault Circuit-Interrupter Protection for Personnel
Ground -fault circuit-interrupter protection for personnel shall be provided as required in 210.8(A) through (D). The groundfault circuit-interrupter shall be installed in a readily accessible location.
(A) Dwelling Units. All 125-volt, single-phase, 15- and 20-ampere recept acles installed in the locations specified in 210.8(A)(1) through (10) shall have ground-fault circuitinterrupter protection for personnel. (6) Kitchens ? where receptacles are installed to serve the countertop surfaces
2014 NEC Handbook Code Commentary; Receptacles installed for disposals, dishwashers, and trash compactors are not required to be protected by GFCIs. A receptacle(s) installed behind a refrigerator is installed to supply that appliance, not the countertop, and is not covered by this GFCI requirement.
(7) Sinks ? where receptacles are installed within 1.8 m (6 ft) of the outside edge of the sink
2014 NEC Handbook Code Commentary; Sinks in kitchens are not the only sinks where a ground-fault shock hazard exists; therefore, this requirement covers all other sinks in a dwelling. any 125-V, 15- or 20-A receptacle installed within 6 feet of a sink located in other than a kitchen is also required to be GFCI protected.
2014 Analysis of Changes; A revision to 210.8(A)(7) for GFCI protection for dwelling unit sinks removes the words ?located in areas other than kitchens? to require GFCI protection for all 125-volt, single-phase, 15- and 20-ampere receptacles installed within 1.8 m (6 ft) of the outside edge of dwelling unit sinks (including kitchen sinks).
For the 2011 NEC, the title was simplified to just ?Sinks,? but excluded kitchen sinks as the GFCI provisions for kitchen sinks was covered at 210.8(A)(6) and this list item only required GFCI protection for receptacles that served a kitchen countertop and did not intend GFCI protection for such things as a receptacle under the kitchen sink for a garbage disposal, even though that garbage disposal receptacle might be within 1.8 m (6 ft) of the outside edge of dwelling unit kitchen sink. Now, for the 2014 NEC, this provision was expanded to all dwelling unit sinks (including the kitchen).
As an example, GFCIprotection will now be required for a receptacle outlet that supplies the
kitchen disposal under the kitchen sink.