If, i'm in a project where using 25% of the transformer & i don't want to use the maximum size of the ocpd at the transfomer's secondary say 125%, i'm afraid if i used a breaker which is sized to 25% of the transformer that will trip because of the inrush current. That leading to another question, if the inrush current equals to 30x flc & of course we don't have such breaker, how the ocpd allows the inrush current when the transformer get ignited?Don't know you can. What are you trying to accomplish?
If, i'm in a project where using 25% of the transformer & i don't want to use the maximum size of the ocpd at the transfomer's secondary say 125%, i'm afraid if i used a breaker which is sized to 25% of the transformer that will trip because of the inrush current. That leading to another question, if the inrush current equals to 30x flc & of course we don't have such breaker, how the ocpd allows the inrush current when the transformer get ignited?
I know this is easy by the LSIG breaker, but what was happened befroe this technology?
If I am interpreting you correctly, the 30x value is the result of the fact that you are using only 25% of the transformer capacity? That would make more sense.If, i'm in a project where using 25% of the transformer & i don't want to use the maximum size of the ocpd at the transfomer's secondary say 125%, i'm afraid if i used a breaker which is sized to 25% of the transformer that will trip because of the inrush current. That leading to another question, if the inrush current equals to 30x flc & of course we don't have such breaker, how the ocpd allows the inrush current when the transformer get ignited?
I know this is easy by the LSIG breaker, but what was happened befroe this technology?
Depends on duration. Here are the numbers I generally look at if I don't have other info:30x is a really high inrush. I thought 6x was a typical design (but I'm going from memory here, maybe is was 12x)?
I suppose you could have a resistor in series during energizing then short it out afterwards. Also using a circuit to switch on peak instead of at zero crossing. Not sure if this is used in non-electronic apps like power transformers. I'll look and see if I have any material on it.Don't know you can. What are you trying to accomplish?
In addition to series resistance and reactors: injection of canceling currents, pre-loading of flux, and sequential phase energization. I'm sure there are more ways.I'll look and see if I have any material on it.
In addition to series resistance and reactors: injection of canceling currents, pre-loading of flux, and sequential phase energization. I'm sure there are more ways.
Yes, there could be some scheme that might be devised, but by the time you incorporate all that, wouldn't it just be easier to have protection on the high side that can ride through the inrush?
I suppose you could have a resistor in series during energizing then short it out afterwards. Also using a circuit to switch on peak instead of at zero crossing. Not sure if this is used in non-electronic apps like power transformers. I'll look and see if I have any material on it.
Of course, as long as the system is stiff enough and shifting the curve does not cause coordination issues.Yes, there could be some scheme that might be devised, but by the time you incorporate all that, wouldn't it just be easier to have protection on the high side that can ride through the inrush?
We adjust the relaying to handle the inrush. Can't remember when we had a problem where unmitigated inrush couldn't be handled by the system. That's why I had to go look to see if there were mitigation solutions for power transformers and there are (I did not look at size constraints).They make NTC current limiting thermistors that accomplish this for small transformers, very commonly used now. When cold, the resistance is high and it limits the current. After the transformer is energized, the NTC thermistor has heated up and the resistance drops to close to nil. Not sure where the size limit stops now however. Used to be only around 3A.
The OP made a comment about using LSIG breakers, I took that to imply this was not a small transformer, i.e. 400A or more on the primary side.
Don't know you can.
Various mitigation techniques are applicable for service transformers as well as large transmission-level transformers.I had to go look to see if there were mitigation solutions for power transformers and there are (I did not look at size constraints).
Put a VFD on the primary side and ramp it in.![]()