JJWalecka
- New England
Does sealing compound come out easily? Will I need to tale a coal chisel to it? Pardon my ignorance
I never found an "easy" way but I've been told an overnight solution of "White Vinegar" will cause it to dissipate.
(I have used that method successfully with mortar mix in conduit)
Some cast, rather than malleable, seal fittings can be rather easy to remove; but, if the compound (cement) is properly listed to be used with an explosionproof seal as required by Sections 501.15(C)(1)&(2), you best be prepared to replace the wiring as well. This is one of the major reasons for removing the explosionproof requirement for Class I, Division 2, boundary seals. Explosionproof seals are still required for Class I, Division 2 enclosures that are required to be explosionpoof.
You may be in luck, with the possible (big) problem that the live conductor has welded to the raceway. If it has, you will definitely need to clean the conduit thoroughly and hope the internal finish hasn't been damaged.Somehow there is a dead short between the hot phase and the conduit, no grounding conductor. Need to remove old conductors and pull in New conductors and reseal with compound.
Since you have to replace the conductors anyway you may as well simply cut the seal fitting off. Replacing an explosionproof seal will now take a properly located explosionproof union, rethreading and reinstalling everything.
I hope to cut the seal off without damaging the threads of the nipple penetrating through the slab??
Or I cut the hole thing off and install an explosion proof union and new seal off, but the rigid is about a 1/2 in from the wall....how will I rethread it without Jack hammering the floor?