Well I did mean here in my area.
You guys use PVC coated rigid for door bell wires right?
Stainless...PVC coated rigid is too cheap.
Well I did mean here in my area.
You guys use PVC coated rigid for door bell wires right?
Stainless...PVC coated rigid is too cheap.
Stainless...PVC coated rigid is too cheap.
Maybe that would be better, but it still is a cable...remember the land of pipe and wire...I thought you used MI cable. Wouldn't want the doorbell to quit working in a fire.
It is almost the only way it is done in this area, there is no code reason not to.
I've seen a ton of specs that only allow MC no longer than 6'...which means the only use for MC would be for fixture whips.
Which means you have to drop whips from J-boxes.
Which means there has to be a ton of access panels in sheetrock ceilings which are ugly and expensive. And always a fight on who furnishes them.
I have sat in meetings with Architects and Engineers arguing my case to allow us to daisy chain above sheetrock ceilings. When I direct their
attention to the access panels over the conference room table, I tell them..."this is what you are telling me you want"....
Daisy chain wins every time.
Fixture tails have edged towards obsolescence with the introduction of 90? C conductors in MC cable. Back in the old days when AC cable had 60? C conductors you needed a tail with higher temperature conductors when using ballasted fixtures. If the job spec is for EMT you won't be jumping MC cable between fixtures.
Every j-box has to be accessible correct? So if your above a sheetrock ceiling you want to limit the use of j-boxes, correct?
It is required by light fixture manufacturer.It's code to have 90 degree wire for fixture tails??
The fixture itself is the access...in most cases it would be a removable fixture.Correct. Your boxes could be flush with the sheetrock & a blank cover. Or if the j-box is above the sheetrock an access door would be required.
The fixture itself is the access...in most cases it would be a removable fixture.
Sorry Iwire.....So your saying if you have say (10) 2x4's you can run the mc directly into the fixtures(daisy chain)? So essentially no need for j-boxes.......in this case? Thanks.
You have to be careful to make sure that's possible, though. A couple of years ago we spec'd some really nice looking fixtures for an upscale commercial install. The lighting rep and manufacturer assured us that this fixture was great for hard-lid ceiling applications.Yes. That is correct. The cables between lights are required to be supported within 6ft of the fixture. Access the connections by removing the ballast cover from below.