Service Size for PV Systems

Status
Not open for further replies.

adsmith

New member
where would i find the code requirements for an appopreatly sized service that would support a 24kw pv array :cool:
 

Smart $

Esteemed Member
Location
Ohio
where would i find the code requirements for an appopreatly sized service that would support a 24kw pv array :cool:
The only concise requirement I can think of is regarding supply side connection (i.e. ahead of service disconnect). 705.12(A), second sentence:

"The sum of the ratings of all overcurrent devices connected to power production sources shall not exceed the rating of the service."

There's no outright requirement for service rating when the PV system is connected to the load side of the service disconnect, but a good general design practice would be the same.

In the case of a 120/240V 24kW system, we're only talking 125A service rating anyway, though it could be a bit greater depending on inverter output rating and sizing the ocpd(s) at not less than 125%.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
where would i find the code requirements for an appopreatly sized service that would support a 24kw pv array :cool:
You should find that the only requirements on service size (unless you are making a line-side tap to connect the PV as mentioned above) will be those set by POCO as part of your interconnect agreement with them.
POCO is usually content with the service size being equal to or greater than the maximum output current of the PV system, but YMMV.
Note that the service current requirements corresponding to your 24kW system will depend on whether your system is delivering straight 240 or balanced 120 or balanced three phase 208Y/120 versus some form of unbalanced output.
And the size of the array (panels) is not relevant. It is the size/output capacity of the inverter(s) that counts. Under some conditions the array can deliver more than its rated power.
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
where would i find the code requirements for an appopreatly sized service that would support a 24kw pv array :cool:
The number you need to start with is the next standard OCPD rating up from 125% of the maximum rated AC output current of your inverter(s), not the DC power rating of the PV array. Are you talking about a backfed breaker in a panel or a supply side tap? If it's a backfed breaker you need to look at 705.12(D)(2), colloquially known as the "120% rule". If it's a supply side tap, then the ceiling is the size of the service.
 
Last edited:

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
The number you need to start with is the next standard OCPD rating up from 125% of the maximum rated AC output current of your inverter(s), not the DC power rating of the PV array. Are you talking about a backfed breaker in a panel or a supply side tap? If it's a backfed breaker you need to look at 705.12(D)(2), colloquially known as the "120% rule". If it's a supply side tap, then the ceiling is the size of the service.
Really not trying to pick nits, but in odd circumstances you could end up satisfying the 120% rule and still exceed the service rating when using backfed breakers. So even in that case there is still the requirement that the number not exceed the rating of the service.
Since adsmith may be starting from a zero knowledge state, I wanted to make the answer more complete. :)
 

Smart $

Esteemed Member
Location
Ohio
Really not trying to pick nits, but in odd circumstances you could end up satisfying the 120% rule and still exceed the service rating when using backfed breakers. So even in that case there is still the requirement that the number not exceed the rating of the service.
Since adsmith may be starting from a zero knowledge state, I wanted to make the answer more complete. :)
Sorry, but I have to disagree. 705.12(A) only applies to a supply side connection.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
where would i find the code requirements for an appopreatly sized service that would support a 24kw pv array :cool:

Regardless of what Art. 705 will allow, a far more limiting factor may be the POCO. Many POCO's have limits that vary with the circumstances for a given site.
 