MC CABLE TO LIGHT FIXTURE
To me a fixture whip only runs to a convenient place for a j-bpx or to the next fixture in a string.
Running all the way to a switch seems more like a wiring method. Is MC ok for the location and length in you case?
Sent from my XT1080 using Tapatalk
Mc is allowed in this case. And it is more of a wiring method. I looked up 410.117 and it says about tap conductors to a light or box 6' or less. I can see that as if I was branching to muilti Lights off one box but see nothing wrong with coming out of a switch to the first light that could be 50' away and daisy chaining lights together.
A tap conductor is one whose ampacity is too low for the upstream protective device. As long as the conductors in the MC are protected against overload by the branch breaker there is no problem. But an undersized (by OCPD) conductor which is large enough for its specific connected load may be allowed under tap or fixture wiring rules.
That is the situation that requires some thought.