what code states that you must use mc in a hospital and not bx
The NEC doesn't state that but what you are looking for is 517.13(A) and 250.118.

It doesn't stop there, you must also have an insulated EGC which will be found in 517.13(B).

IOW's, it's not just plain AC that is needed, it will need to be an HCFC