120 - 25 = 95. Close enough for most purposes. If the bulb filament is really cool, the current may be even higher and the drop across the bulb even lower.What would be the voltage drop across the lamp?
I make it 89 volts. But then, I am taking into account that in addition to the 8' ground rod described in the first post, the current cannot return to the source without first passing through the other ground rod, the one associated with the building's service. That makes the total resisance (assuming both ground rods have the same resistance to ground) of 50 ohms. Here's the math:What would be the voltage drop across the lamp?
Only one problem, the current has to travel through the rod the lamp is attached to, but once current enters the earth which path(s) (which electrodes) will it flow through to return to the source? Not very likely 100% of that current returns via a single rod only, which makes measuring the resistance beyond the first rod a difficult task to achieve any accuracy on.I make it 89 volts. But then, I am taking into account that in addition to the 8' ground rod described in the first post, the current cannot return to the source without first passing through the other ground rod, the one associated with the building's service. That makes the total resisance (assuming both ground rods have the same resistance to ground) of 50 ohms. Here's the math:
- P = VxV/R
 - Thus R = VxV/P
 - R = 120 x 120/100 = 144.
 - So the resistance of the light bulb is 144 ohms.
 - You have a series circuit with the light bulb and two ground rods in series with the breaker.
 - Total resistance is 144 + 50, or 194 ohms.
 - Current is therefore 120 volts divided by 194 ohms, or .619 amps.
 - Voltage across the light bulb is .619 amps times 144 ohms, or 89 volts.
Its not that dangerous unless you're close to the rod where the light/power is attached. My dad made a similar device to collect worms for fishing. The current in the earth pushed them to the surface near the rod. Stupid kid me had to poke my finger into the ground and I could feel the buzz -- my knees were well away from the rod and I poked my finger into the ground probably 2' from it. I then understood why the worms came to the surface.
Sounds like a Jame's Bond or MacGyver Ground Rod Test Set to me. Very foolish to do such a thing and dangerous. Using earth as a conductor is forbidden unless you are a utility operating at very high voltage.
Remind the student he is grounded, but don't say he is safe, this will add confusion and is inaccurate. You could possibly tell him he is "allegedly" safe and then have him disprove that theory.Now ask the student this. Turn off the breaker and cut the wire mid span somewhere. Take one wire in one hand, and the other end in the other hand and have someone turn on the breaker. Remind the student he is grounded and safe. What happens? :angel:
It was humor.Remind the student he is grounded, but don't say he is safe, this will add confusion and is inaccurate. You could possibly tell him he is "allegedly" safe and then have him disprove that theory.