EuropeBut where are you going to find all the gizmos in your house that can use 240?
Appliance shopping involves a vacation as well, should make many very happy wives:happyyes:
EuropeBut where are you going to find all the gizmos in your house that can use 240?
If we dispense with MGN, we may perhaps have to increase the rating of surge arresters, increase the insulation level of equipment to protect against surges: costly undertaking indeed.
Europe
Appliance shopping involves a vacation as well, should make many very happy wives:happyyes:
Are you talking about faults due to lightning surges or about power frequency faults?Don't bet on that. The rapid rise and fall times of a fault represent a very high frequency for which there is no such thing as a low impedance.
Because the tungsten bulb presents a non-linear resistance, the voltage drop can not be calculated readily with any formula as in post #6 but only be measured.What would be the voltage drop across the lamp?
The 100 watt lamp connected as described in the first post will light but not at full brightnes.
The actual voltage on the lamp cant be readily calculated for at least three reasons
Firstly we dont know the actual resistance of the lamp filament, which varies according to the temperature.
Secondly although the ground rod resistance is given, the current flows through TWO ground rods, and we are not given the resistance of the other ground connections at the transformer or service entrance.
Thirdly, to be really accurate we need to know the resistance of the wires, and what the ACTUAL voltage is, not just the nominal voltage.
So...am I the only one waiting for somebody to say
"OK, I just ran outside and did this, and here's the amps, voltage, and brightness of the lamp I used..."
![]()
Well in Dallas we have 2 inches of powder snow and 20 degrees this morning. Never seen it get so cold down here, especially this late in the season. Yesterday morning it was 11 degrees. :rant:Well, we have almost 2 feet of snow and ice on the ground and it's 11 degrees F.
Well, we have almost 2 feet of snow and ice on the ground and it's 11 degrees F.
Get back to me in a couple months.
Probably a computer might have created the approximate equation P = V^1.6/21.22 after having input data of V-I characteristics of various filament bulbs for an operating voltage range of 90 to 130 V and an algorithm to fit the power values within 1/2 W at 90 V and 3/4 W at 130 V of the actual power values.For a nominal 120 V 100 W bulb this is approximately P = V^1.6/21.22 .
The equation is quite close for a range from 90 to 130 V for an experiment with a different bulb at a different time. In this case the error was less than 1/2 W at 90 V and 3/4 W at 130 V.
.